ich habe heute meine ersten Geräte aktiviert:
3x Victron Multiplus II 5000
1x Cerbo GX
Soweit so gut, ein Problem stellt sich mir in den Weg...
Die rote LowBattery Anzeige blinkt obwohl ich 53V anliegen habe...
Settings aller MPIIs:
TAB: General
System frequency 50Hz
Shore current 50.0 A
Overruled by remote checked
Dynamic current limiter unchecked
External current sensor connected (see manual) unchecked
State of charge when Bulk finished 95.0 %
Battery capacity 608 Ah
Charge efficiency 0.95
TAB: Grid
Country / grid code standard Germany: VDE-AR-N 4105:2018-11, internal NS protection
LOM detection AC input 1 Type B (grid code compliant)
rise-in-voltage protection U> 253.0 V
start network service HF treshold 50.20 Hz
P(f>) droop 5.00 %
Use Aux1 as disable FeedIn signal checked
Maximum AC current for charge or feed in 100.0 %
Reactive power regulation Use a fixed Cos Phi
Filter time for reactive power 3.3 s
Cos phi at point 1 1.00
TAB: Inverter
PowerAssist unchecked
Inverter output voltage 230 V
State Of Charge shut-down 10.0 %
State Of Charge restart 20.0 %
Inverter DC shut-down voltage 44.80 V
Inverter DC restart voltage 49.60 V
Low DC alarm level 49.60 V
Do not restart after short-circuit (VDE 2510-2 safety) unchecked
enable AES unchecked
TAB: Charger
Enable charger checked
Weak AC input unchecked
Stop after excessive bulk unchecked
Lithium batteries checked
Configured for VE.Bus BMS unchecked
Charge curve Adaptive
Absorption voltage 56.00 V
Float voltage 52.80 V
Charge current 60 A
Repeated absorption time 1.00 Hr
Repeated absorption interval 7.00 Days
Maximum absorption time 4 Hr
TAB: Virtual switch
TAB: Usage
Virtual switch usage Do not use VS
TAB: Assistants
TAB: Assistant Configuration
ESS (Energy Storage System) (size:985)
) System uses LiFePo4 with other type BMS
(This can be either a BMS connected via CAN bus or a BMS system in which the
batteries are protected from high/low cell voltages by external equipment.)
) The battery capacity of the system is 608 Ah.
) Sustain voltage 50.00 V.
) Cut off voltage for a discharge current of:
0.005 C= 52.00 V
0.25 C= 50.00 V
0.7 C= 49.20 V
2 C= 48.00 V
) Inverting is allowed again when voltage rises 1.20 V above cut-off(0).
) Relevant VEConfigure settings:
- Battery capacity 608 Ah.
- PowerAssist unchecked
- Lithium batteries checked
- Dynamic current limiter unchecked
- Storage mode unchecked
Total size of all assistants including the required
(hidden) system assistants is: 1044
bist du bei diesem Thema schon weiter gekommen?
Ich habe habe nämlich das gleiche Problem.
Viele Grüße
ja bin ich. Nachdem ich AC-IN angeschlossen hatte, lief es.
Aber mittlerweile gibt es eine neue Firmware, V467 => Nach den Release Notes gab es da ein Problem in der Richtung.
